GlennCMC70
post Nov 9 2008, 02:19 AM
Post #1


Veteran Member
*****

Group: Member
Posts: 2,688
Joined: 23-December 03
From: Ft Worth, TX
Member No.: 8



there is no 220V service in my garage - thats about to change.

i picked up a 250V 30A outlet (3 slots arranged in a circle w/ one looking like a "L") which matches the plug on the welder.
i have a 30A breaker that takes up two slots in the breaker panel for the house (located in the garage!)
i have some new 10 gauge 3 conductor wire (black, white, and green conductors).
snap the breaker in place - make sure its switched off.
install a black and white conductor in one of the two set screw slots in the 30A breaker.
connect the other ends of the black/white to the outlet and the ground to the ground on the back of the outlet and inside the breaker panel (metal box).


to be honest here, the only thing i know about A/C electricity is it can kill you. other than that, i don't know jack. i can replace a bad outlet/socket/switch, but i couldnt wire any 110v circuit from the box to the wall if i had to.

so does the above sound right? i know there should normally be a red wire to use in place of the white, but i've read thats really only required for 4 prong plug/outlets.

looking for the FRAXX guidance here oh wise one's. (IMG:http://www.frrax.com/rrforum/style_emoticons/default/drink.gif)
Go to the top of the page
 
+Quote Post
 
Start new topic
Replies
nape
post Nov 11 2008, 04:21 AM
Post #2


Veteran Member
*****

Group: Advanced Members
Posts: 2,511
Joined: 14-November 04
From: Homer Glen, IL
Member No.: 540



As ironic as this is going to sound, I had an electrical issue at the hotel I'm staying at tonight.

I started noticing a "zip zip" or "bzzzt" sound. At first, I thought it was just the hard drive on my laptop which was on the desk and I was sitting on the bed. Then, my laptop went to sleep and I still noticed the sound but it was coming from the direction of the door. After a while, I noticed it seemed to be coming from the wall outlet. Sure enough, I turned off the lights in the room and could see an arc behind the trim plate.

Yet another irony, I left my tool bag in the back of another guy's truck today so I brought them into my room for the night. So, I took off the trim plate and the hot wire on the receptacle is arcing away and melting the recept. I went up to the front and talked to the desk girl (who likes us, 8 guys from the contractor are staying here). I didn't want to move rooms so I offered to fix it for the night.

Anyway, the issue with the wiring is that the lazy (or unknowing) person who wired this place up didn't bother to pig tail the recepts and just decided to hook and go on each side of the recept. The problem with this technique is that it puts the device in series with the circuit and depends on the device to take the load of everything on the circuit, not just what is on that recept. The other issue that I found is that the convenience recepts for the same room number on different floors (ex. 102, 202, 302) share the same circuit. Therefore, there is the opportunity for 3 mini fridges, 3 microwaves, 3 alarm clocks, 9 lamps plus whatever the renter plugs in to be on the same 15A breaker on #14 wire.

Oh, and I forgot to mention, I found out the whole place is wired in Romex.

Are you glad that the owner of the building was able to save money building the place now that you know some of what goes on? Strict codes may cost more initially, but piece of mind is worth it in the long run. The same goes for the trained craftsmen that build these buildings and know the codes vs. guys off the street with a pair of wire strippers.

Support your local IBEW Electricians and build Union (IMG:http://www.frrax.com/rrforum/style_emoticons/default/wink.gif)

PS- I used the microwave to make mini pizzas tonight. Tomorrow, I think I'll go to Subway and leave the electrical work at work. (IMG:http://www.frrax.com/rrforum/style_emoticons/default/wink.gif)

This post has been edited by nape: Nov 11 2008, 04:24 AM
Go to the top of the page
 
+Quote Post
Torque
post Nov 11 2008, 05:25 AM
Post #3


Member
*

Group: Advanced Members
Posts: 108
Joined: 10-August 07
Member No.: 1,886



QUOTE (nape @ Nov 10 2008, 08:21 PM) *
Anyway, the issue with the wiring is that the lazy (or unknowing) person who wired this place up didn't bother to pig tail the recepts and just decided to hook and go on each side of the recept. The problem with this technique is that it puts the device in series with the circuit and depends on the device to take the load of everything on the circuit, not just what is on that recept. The other issue that I found is that the convenience recepts for the same room number on different floors (ex. 102, 202, 302) share the same circuit. Therefore, there is the opportunity for 3 mini fridges, 3 microwaves, 3 alarm clocks, 9 lamps plus whatever the renter plugs in to be on the same 15A breaker on #14 wire.

Oh, and I forgot to mention, I found out the whole place is wired in Romex.

Are you glad that the owner of the building was able to save money building the place now that you know some of what goes on? Strict codes may cost more initially, but piece of mind is worth it in the long run. The same goes for the trained craftsmen that build these buildings and know the codes vs. guys off the street with a pair of wire strippers.

Support your local IBEW Electricians and build Union (IMG:http://www.frrax.com/rrforum/style_emoticons/default/wink.gif)

PS- I used the microwave to make mini pizzas tonight. Tomorrow, I think I'll go to Subway and leave the electrical work at work. (IMG:http://www.frrax.com/rrforum/style_emoticons/default/wink.gif)


Wow, that's intense. By pigtail, does that mean you have a hot, neutral and ground wire already screwed (solidly) into the receptacle and you use a wire nut to join the pigtail and the other up and downstream (for lack of a better term) wires rather than using all the screws on the receptacle to secure the wires? Is that usually a code thing or just a best practice?

Glad you made it out ok and hope at least the smoke detector works in that place.
Go to the top of the page
 
+Quote Post
nape
post Nov 11 2008, 11:11 PM
Post #4


Veteran Member
*****

Group: Advanced Members
Posts: 2,511
Joined: 14-November 04
From: Homer Glen, IL
Member No.: 540



QUOTE (Torque @ Nov 10 2008, 11:25 PM) *
Wow, that's intense. By pigtail, does that mean you have a hot, neutral and ground wire already screwed (solidly) into the receptacle and you use a wire nut to join the pigtail and the other up and downstream (for lack of a better term) wires rather than using all the screws on the receptacle to secure the wires? Is that usually a code thing or just a best practice?

Glad you made it out ok and hope at least the smoke detector works in that place.


Correct, that's what I mean by pigtail. The other thing is that wire nuts are just "splice caps". Some wire nuts claim to be able to make a correct splice by just putting 2, 3, etc wires inside then just turning. That's BS, you should always twist the wires clockwise with a pair of side cutters (lineman's pliers, etc) to make your splice, then tighten the wire cap on clockwise to cover the connection. That way, you have a chance of working it hot if you need to and the splice won't open up just by taking the wire cap off.

As far as not hooking two wires on a side and/or terminal, it is best practice always and it is code in Chicago. The same goes for stabbing solid wire in the holes on the back of the receptacle, best practice to not do it and it's illegal by Chicago code. It's more likely to loosen up over time and at that point there isn't anything holding it in. At least by making a hook on the wire (clockwise) and putting it under a side screw, it's less likely to come off even if it does loosen up.

Also, when stripping solid wire (which includes Romex) practice not knicking the wire. A knick in the wire is a pre-failure and if you do have a problem or when the wire becomes old and brittle, it'll be most likely to fail there.

ALWAYS, Hot on top, ground down. - meaning, put the hot wire on the top brass colored screw if mounted vertical or either screw mounted horizontal, the neutral on the lower silver screw if mounted vertical or the opposite silver screw if mounted horizontal, and the ground screw should be down or on the bottom.

If everyone would follow the rules, this stuff would be easy...
Go to the top of the page
 
+Quote Post

Posts in this topic
GlennCMC70   Installing a 220V circuit for a 220V welder - need help.   Nov 9 2008, 02:19 AM
trackbird   Sounds about right. Make sure you run the ground l...   Nov 9 2008, 02:35 AM
GlennCMC70   good. now any advice on running a temp run across...   Nov 9 2008, 02:42 AM
trackbird   I ran mine through the studs. If not, I'd put ...   Nov 9 2008, 03:21 AM
sgarnett   I used metal conduit and a metal outlet box for my...   Nov 9 2008, 03:34 AM
GlennCMC70   i plan to use the PVC outdoor stuff. thanks guys.   Nov 9 2008, 03:59 AM
Wayno   Is you're panel mounted between the studs ...   Nov 9 2008, 04:15 AM
GlennCMC70   between two studs "in" the wall. i was ...   Nov 9 2008, 04:21 AM
FBody383   When I ran mine I had about 20' of wire left o...   Nov 9 2008, 05:41 AM
GlennCMC70   this used welder came w/ a 20' plus cord on it...   Nov 9 2008, 05:52 AM
Torque   Not an electrician but I can tell you how I most r...   Nov 9 2008, 06:55 AM
Torque   the wire i have turns out to be 14-3 and not the 1...   Nov 9 2008, 07:20 AM
sgarnett   220V dryers and ovens get a neutral, because they ...   Nov 9 2008, 03:14 PM
GlennCMC70   QUOTE (sgarnett @ Nov 9 2008, 09:14 AM) 2...   Nov 9 2008, 03:18 PM
GlennCMC70   accually the way i understand it is the neutral is...   Nov 9 2008, 03:16 PM
nape   I AM an electrician and Sean's advice is corre...   Nov 9 2008, 04:50 PM
Torque   Out of curiosity, what's the safety issue with...   Nov 9 2008, 05:46 PM
nape   QUOTE (Torque @ Nov 9 2008, 11:46 AM) Out...   Nov 9 2008, 09:41 PM
GlennCMC70   got it done. usd the black and red to the 30A brea...   Nov 9 2008, 07:07 PM
nape   QUOTE (GlennCMC70 @ Nov 9 2008, 01:07 PM)...   Nov 9 2008, 09:49 PM
sgarnett   QUOTE (nape @ Nov 9 2008, 04:49 PM) The s...   Nov 11 2008, 05:20 AM
Torque   Thanks for the explanation on Romex. The melting ...   Nov 10 2008, 04:20 AM
nape   QUOTE (Torque @ Nov 9 2008, 10:20 PM) Tha...   Nov 11 2008, 04:37 AM
firehawkclone   This tread came at the perfect time. I've need...   Nov 10 2008, 03:56 PM
nape   As ironic as this is going to sound, I had an elec...   Nov 11 2008, 04:21 AM
Torque   QUOTE (nape @ Nov 10 2008, 08:21 PM) Anyw...   Nov 11 2008, 05:25 AM
nape   QUOTE (Torque @ Nov 10 2008, 11:25 PM) Wo...   Nov 11 2008, 11:11 PM
Torque   QUOTE (nape @ Nov 11 2008, 03:11 PM) QUOT...   Nov 12 2008, 12:17 AM
TOO Z MAXX   QUOTE (nape @ Nov 10 2008, 11:21 PM) As i...   Nov 12 2008, 06:15 AM
nape   QUOTE (TOO Z MAXX @ Nov 12 2008, 12:15 AM...   Nov 12 2008, 11:47 PM
marka   Howdy, First time I ever heard anything bad (safe...   Nov 12 2008, 01:51 PM
sgarnett   On the shoeless cobbler's kids topic, I screwe...   Nov 12 2008, 02:51 PM
Machine   2 things that I was thinking regarding your applic...   Nov 12 2008, 08:24 PM
nape   QUOTE (Machine @ Nov 12 2008, 02:24 PM) D...   Nov 12 2008, 11:29 PM